Quote Originally Posted by kjsphoto
Awesome idea!

DO youthink that the 3x5 foot enlarger area will suffice? I am putting in the electrical boxes tommorrow and running wire. I will stagger the darkroom plugs on 2 breakers so every other one is on a seperate breaker (2 total).

ALso isnt is 1 100 watt bulb = 1 amp? So basically you can have 15 lights on 1 breaker correct?
Sounds good on both points and yes 100 watts at 100 volts is 1 amp. Be sure the plugs are high on the wall so they are easy to access. Especially keep them high around the wet side.